Thermistor replacement

lourph

Active member
Jun 10, 2024
32
venice, fl
I have an ultra temp heat pump that says the actual water temp is the same as the set temp of 104 on the heat pump panel. I was under the impression that this panel was inactive because everything is connected to the Easy Touch automation. Pentair told me to try to replace the thermistor. I can see it looking down from the fan. Is that something I can change or do I need a pool repairman? It looks complicated removing to remove the cover to get to the thermistor. Thanks
 
This is entirely dependent on your comfort levels with such things. I would not hesitate and am totally comfortable around equipment both inside and out.

1719673339659.png
 
It doesn’t look bad to open the panel and replace the thermistor. However, where do I plug the thermistor in? It looks like it goes into the box behind the heat pump control panel. That looks more complicated to remove. Can I splice the wires instead ? Thanks
 
Remove the panels and follow the yellow wire from the thermistor to the control board.

Route the new wire the same as the old wire.

Note: Do not do anything unless you are 100% sure you can do it safely.

Make sure all breakers are off and verify that there is no power with a multimeter.
1719844985300.png


1719844674936.png

1719844698606.png
 
Drain the heater before removing the thermistor to avoid water getting into the unit.

Crack open the union to drain.

Perform the following steps to completely drain the heat pump.
1. Turn off the electrical power to the heat pump at the main breaker panel.
2. Shut off the water supply to the heat pump.
3. Disconnect the water inlet and outlet unions located on opposite sides of the heat pump

1719846151527.png
 