A fellow Mastertemp owner here. A practice that can cause early failure is running the heater with the water consistently cold. (The manual says 68F, which is 20C.) This causes combustion gasses to condense in the heater, and they're quite acidic.
 
Yes the gas tech said the pressure was good.
Saying the pressure is good does not tell us anything to diagnose your problem. We need to know the numbers before and after the heater starts.

A heater should last 5 to 15 years. The people who you say are qualified should be able to diagnose the root cause and not simply throw up their hands and replace one heater after another. Are any of the people who touched your heater NATE certified?


If you cannot dig into the details of the heater then you need to find someone who will.

Are you capable of dissembling the heater?

What does Penatir say about your problems?
 
A fellow Mastertemp owner here. A practice that can cause early failure is running the heater with the water consistently cold. (The manual says 68F, which is 20C.) This causes combustion gasses to condense in the heater, and they're quite acidic.
Thanks. The water temp is set to about 84F. So if never dips below 74F ish when the pool is open. Don’t think that would do it. A heater a season is crazy. Is your pool salt or chlorine?
 
Thanks. The water temp is set to about 84F. So if never dips below 74F ish when the pool is open. Don’t think that would do it. A heater a season is crazy. Is your pool salt or chlorine?
It's been both. The heater was reportedly 2 years old when we bought the house in summer 2020, I'm pretty sure using liquid chlorine because the salt system was broken. Fixed that and have been using the salt system for 5 years now April to November. The rest of the year it's pucks in a floater. Note the salt was about 1500 even before boosting it to start running the cell. Unfortunately the first ~4 months I did not realize it was important that the plumbing had the generator before the heater. I was new to pools and learning. (Don't trust home inspectors.) Fixed that asap, but have been expecting a shortened life. So far (fingers crossed, knocking on wood) all good at 7 years. During the 4 months, we still had a big single-speed pump putting ~90 gpm through the system. This probably helped.

In case useful, our normal is CYA 60-70, FC 7-10, pH 7.3-8.0, TA 60, CH 400. One other detail is we only use the heater for the attached spa for maybe 60 hours of operation per year max.

Trust the experts here. They've helped me through several pool adventures.

One other low probability is some kind of unusual galvanic action. The heater must be bonded.
 
Last edited:
It's been both. The heater was reportedly 2 years old when we bought the house in summer 2020, I'm pretty sure using liquid chlorine because the salt system was broken. Fixed that and have been using the salt system for 5 years now April to November. The rest of the year it's pucks in a floater. Note the salt was about 1500 even before boosting it to start running the cell. Unfortunately the first ~4 months I did not realize it was important that the plumbing had the generator before the heater. I was new to pools and learning. (Don't trust home inspectors.) Fixed that asap, but have been expecting a shortened life. So far (fingers crossed, knocking on wood) all good at 7 years. During the 4 months, we still had a big single-speed pump putting ~90 gpm through the system. This probably helped.

In case useful, our normal is CYA 60-70, FC 7-10, pH 7.3-8.0, TA 60, CH 400. One other detail is we only use the heater for the attached spa for maybe 60 hours of operation per year max.

Trust the experts here. They've helped me through several pool adventures.

One other low probability is some kind of unusual galvanic action. The heater must be bonded.
Thanks for the tips and info. My water chemistry is similar to yours but my chlorine levels are a lot lower and my salt is at 3100. The usage is likely 3-5 hours a day as I have a shady backyard. So the total time will add up through the season, I don’t think it’s too much though. There is a chance my last two heaters were unlimited and real manufacturer defects.
 
Saying the pressure is good does not tell us anything to diagnose your problem. We need to know the numbers before and after the heater starts.

A heater should last 5 to 15 years. The people who you say are qualified should be able to diagnose the root cause and not simply throw up their hands and replace one heater after another. Are any of the people who touched your heater NATE certified?


If you cannot dig into the details of the heater then you need to find someone who will.

Are you capable of dissembling the heater?

What does Penatir say about your problems?
Pentair sends the tech in and then the tech says the heater has a manufacturer defect. I can dissemble the heater to a certain point, what are you asking me to do? I can get the numbers you are asking for when I open the pool.
 
Hi. Thank you for your response. I tried to upload higher res but it doesn’t let me go higher than 1MB. I’ll try to do better. Those last two pics are from the last failure. In the one picture you can see some rust staining on the drum and a broken seal. And the first picture you can see the blower intake blows off. Was just showing that. The gas line coming in is a 1” line, picture attached. The heater is a 125, so a 125,000 BTU. Professionally installed by a recommended installer of Pentair. Not sure what else to say. I’ve gone through 3 in 4 years.
Your gas line is a 3/4" line, you measure the inside diameter.
Has anyone checked the incoming gas pressure? If it is too high, it will "blow" past the main gas valve when it is open (it can only regulate a certain amount of pressure measured in inches of water column, with a maximum of 10 or .037 psig.) and fill the combustion chamber so fast that you can get "explosive" combustion that can blow the venturi off the air blower. Have only ever heard of it one other time, and those heaters have been around for over 30 years.
 
  • Like
Reactions: Latch
Your gas line is a 3/4" line, you measure the inside diameter.
Has anyone checked the incoming gas pressure? If it is too high, it will "blow" past the main gas valve when it is open (it can only regulate a certain amount of pressure measured in inches of water column, with a maximum of 10 or .037 psig.) and fill the combustion chamber so fast that you can get "explosive" combustion that can blow the venturi off the air blower. Have only ever heard of it one other time, and those heaters have been around for over 30 years.
I’m going to ck these numbers and the incoming gas pressure. Thank you.
 
There is actually a specific gas pressure check process that involves three measurements -

  1. Static pressure relative to atmospheric pressure on the input side (typically no higher than 11-14” WC)
  2. Dynamic pressure relative to atmospheric pressure on the input side (once the heater is running), typically no less than 4” WC but no higher than 9” WC
  3. Pressure differential across the valve (typically -0.2” WC)
These gas pressure conditions need to be satisfied or else the combustion will either be lean or, in your case, explosively rich.

You also should know what your incoming utility service provides - gas pressure and maximum flow rate. There are many different options for residential gas setups and sometimes the output of the gas meter is setup to be a “high” pressure line that then needs to be regulated at the particular appliance. It is entirely possible that your service pressure is too high and that is causing these failures. Only a properly certified gas plumber can and should do these checks.
 
  • Like
Reactions: 1poolman1 and Latch

Enjoying this content?

Support TFP with a donation.

Give Support
Had an above ground pool installer in today and he said that the pool isn’t bonded. I had no idea. He mentioned this can cause Galvanic Corrosion, rapid corrosion of any metal parts. Is it possible this has also damaged my pool heater?
 
Had an above ground pool installer in today and he said that the pool isn’t bonded. I had no idea. He mentioned this can cause Galvanic Corrosion, rapid corrosion of any metal parts. Is it possible this has also damaged my pool heater?

What model pool are we discussing?

It will be obvious if you have galvanic corrosion anywhere around your pool.

Bonding does not prevent galvanic corrosion. Sacrificial anodes can prevent galvanic corrosion.


And no, lack of bonding did not cause the heater problems you have been having.

 
  • Like
Reactions: 1poolman1
Thanks for the info and links. I have no corrosion like that around the pool. I have an all resin above ground pool, the only metal is the shell. I will still have it bonded at the seem. Thanks again