Hayward Omni Logic alarm, No Water Flow Timeout FlowSensor

Manasco

New member
May 30, 2022
2
24540
Pool Size
8000
Surface
Fiberglass
A few days ago my varible speed pump began running for approximate 15 minutes and then shutting down. The Timeout alarm is displayed in the panel and on my phone application. I have cleaned the filter and baskets and checked that all valves are as they should be. The pump does not appear to be over heating, it is not hot to touch after shut down. I know that my T cell needs to be replaced, could that be the reason the pump is being shut down?
 
Welcome to TFP.

Is your SWG flow sensor properly connected to the Omni panel. The Omni panel uses the SWG flow sensor and if it sees no flow it shuts off the pump.

I think in CONFIGURATION you can tell the Omni there is no flow sensor.
 
Last edited:
A few days ago my varible speed pump began running for approximate 15 minutes and then shutting down. The Timeout alarm is displayed in the panel and on my phone application. I have cleaned the filter and baskets and checked that all valves are as they should be. The pump does not appear to be over heating, it is not hot to touch after shut down. I know that my T cell needs to be replaced, could that be the reason the pump is being shut down?
Thanks for the reply. I found that it was a bad flow sensor. Omnilogic will shut down the pump after the 15 minutes it allows for priming if it is being told there is no flow.
 