Variable Speed pool pumps the pros and cons as I see them.
In 2019 my old single speed 110 V AC pump started leaking and had to be replaced. I was 'persuaded' that the way to go was by replacing it with a variable speed Pentair pool pump that cost around $1,000 as they allegedly would pay for themselves in a few years by savings on electricity bills. 3 years on I've seen little difference in running costs and for the past year a lot of aggravation with the old GFCI tripping. So far its cost me over $1,000 to get a new GFCI & Housing fitted next to the pump and new cable to the main panel to meet current code but the tripping issue is still present. So is the problem the pump ?
Here lies the problem that I see as, variable speed pumps cost a lot more than a 110 volt (or 230 volt) simple induction motor pump as first the 110 volts AC has to be rectified to 110 DC which is then used to power a variable frequency inverter (drive) that supplies an induction motor with a variable frequency & voltage drive depending on the selected RPM by the user. At stop the frequency is 0 Hz and there is no voltage but both parameters are ramped up to give a pump RPM of around 1500 RPM for low speed lower energy use for most of the time and up to 3450 RPM for high speed when cleaning the pool.
That's the advantages but there is one parameter that seems to be overlooked and that's the design of the inverter for pool pumps when GFCI's have to be used. Sold state inverters have been around a long time for battery back up with computers and its worth starting there to look at a potential downside. You can purchase 1500 VA UPS (Uninterrupted Power Supply) for around $200 that when your power goes off, you can run a desktop computer for up to 1 hour from a UPS which have 2 small lead acid batteries, a charger to keep them charged up and a fixed frequency/voltage Inverter to convert 12 Volts (or 24v) to 110 volts when main power goes.
The AC from your electricity company is a pure sine way and normally there is no 'noise' or interference present that affects any household equipment. In rare cases, one can fit line filters to clean it up if there's a problem. However, inverters are 'noisy' by nature due to the fact that the simulated sine wave is created by high power semiconductors turning a DC voltage on and off at different levels, intervals and different points along the 360 degrees of a sine wave. Whilst power from the electricity company comes from from turbine/generators and produces a perfect sine wave, the simulated sine wave from inverters is a 'stepped' sine wave and that produces noise. For most appliances, like phone/tablet chargers, computers, lap tops, TV's, Hobs, Ovens etc the noise has no effect, however there is some anecdotal evidence that noise from the pumps inverter might trip GFCI's. It should be noted that pump inverters that vary their frequency output will produce 'noisier' sine wave at lower RPM (frequency) than at a higher RPM or frequency.
The rated power of this pump is claimed to be a max of 12 amps or so, far more than one used in a UPS which always runs at 60 Hz anyway.
So far I've tried new cabling, a new GFCI, ferrite noise suppressors on the 3 wires between the pump and GFCI and still it trips at random every day or so. Perhaps if this Pentair Pump remembered the time I could live with it but like Microwave ovens it doesn't remember the time.
One other oddity is when the pump first comes on in the morning. Its supposed to go full speed at 3500 or full speed to prime the pump and then go to program 1 of 3. It does that as the RPM drops to 2500 which I have it set for but a few minutes later the pump will stop, wait 10 secs or so and then ramp up again. It may repeat this for 3-5 times before settling down and running normally unless a random trip happens.
I've had two attempts to get answers from Pentair about this odd behavior with no explanation and as far as the GFCI is concerned I've got nowhere. A blog site reports similar issues over the GFCI with claims that Pentair recommend Siemens GFCI's rather than Squard D GFCI's. The response I got from Pentairs support site over GFCI's was -
"Also regarding the breaker we do test all units with siemens breakers and they work the best for our units. we highly recommend using the, and the correct size as well"
Needless to say there was NO warning to use Siemens GFCI's rather than SquareD in the installation guide and their response doesn't highlight a problem with SquareD.
In conclusion -
Is it a GFCI incompatibility issue ? I don't know and Pentair refuse to comment !
Have the electronics gone crazy in the Pump ? It might be as the tech guy couldn't explain that peculiar start up sequence where it started and stopped for no reason.
So, I'm junking this over prices and worthless VS pump and fitting a simple 2 speed pump at 1/3rd the cost and while I'm at it, I'll have installed an Alexa ready Wi-Fi timer at waist height instead of getting down on my knees to use the crappy key pad that's on the pump. At least I can use my phone to change times if needed.
I forgot to mention, its a very noisy pump this Pentair pump compared to the ancient one that died in 2019 after giving good service. If anyone knows of a fix or suggestion, I'd welcome it.
Thanks - Mike
In 2019 my old single speed 110 V AC pump started leaking and had to be replaced. I was 'persuaded' that the way to go was by replacing it with a variable speed Pentair pool pump that cost around $1,000 as they allegedly would pay for themselves in a few years by savings on electricity bills. 3 years on I've seen little difference in running costs and for the past year a lot of aggravation with the old GFCI tripping. So far its cost me over $1,000 to get a new GFCI & Housing fitted next to the pump and new cable to the main panel to meet current code but the tripping issue is still present. So is the problem the pump ?
Here lies the problem that I see as, variable speed pumps cost a lot more than a 110 volt (or 230 volt) simple induction motor pump as first the 110 volts AC has to be rectified to 110 DC which is then used to power a variable frequency inverter (drive) that supplies an induction motor with a variable frequency & voltage drive depending on the selected RPM by the user. At stop the frequency is 0 Hz and there is no voltage but both parameters are ramped up to give a pump RPM of around 1500 RPM for low speed lower energy use for most of the time and up to 3450 RPM for high speed when cleaning the pool.
That's the advantages but there is one parameter that seems to be overlooked and that's the design of the inverter for pool pumps when GFCI's have to be used. Sold state inverters have been around a long time for battery back up with computers and its worth starting there to look at a potential downside. You can purchase 1500 VA UPS (Uninterrupted Power Supply) for around $200 that when your power goes off, you can run a desktop computer for up to 1 hour from a UPS which have 2 small lead acid batteries, a charger to keep them charged up and a fixed frequency/voltage Inverter to convert 12 Volts (or 24v) to 110 volts when main power goes.
The AC from your electricity company is a pure sine way and normally there is no 'noise' or interference present that affects any household equipment. In rare cases, one can fit line filters to clean it up if there's a problem. However, inverters are 'noisy' by nature due to the fact that the simulated sine wave is created by high power semiconductors turning a DC voltage on and off at different levels, intervals and different points along the 360 degrees of a sine wave. Whilst power from the electricity company comes from from turbine/generators and produces a perfect sine wave, the simulated sine wave from inverters is a 'stepped' sine wave and that produces noise. For most appliances, like phone/tablet chargers, computers, lap tops, TV's, Hobs, Ovens etc the noise has no effect, however there is some anecdotal evidence that noise from the pumps inverter might trip GFCI's. It should be noted that pump inverters that vary their frequency output will produce 'noisier' sine wave at lower RPM (frequency) than at a higher RPM or frequency.
The rated power of this pump is claimed to be a max of 12 amps or so, far more than one used in a UPS which always runs at 60 Hz anyway.
So far I've tried new cabling, a new GFCI, ferrite noise suppressors on the 3 wires between the pump and GFCI and still it trips at random every day or so. Perhaps if this Pentair Pump remembered the time I could live with it but like Microwave ovens it doesn't remember the time.
One other oddity is when the pump first comes on in the morning. Its supposed to go full speed at 3500 or full speed to prime the pump and then go to program 1 of 3. It does that as the RPM drops to 2500 which I have it set for but a few minutes later the pump will stop, wait 10 secs or so and then ramp up again. It may repeat this for 3-5 times before settling down and running normally unless a random trip happens.
I've had two attempts to get answers from Pentair about this odd behavior with no explanation and as far as the GFCI is concerned I've got nowhere. A blog site reports similar issues over the GFCI with claims that Pentair recommend Siemens GFCI's rather than Squard D GFCI's. The response I got from Pentairs support site over GFCI's was -
"Also regarding the breaker we do test all units with siemens breakers and they work the best for our units. we highly recommend using the, and the correct size as well"
Needless to say there was NO warning to use Siemens GFCI's rather than SquareD in the installation guide and their response doesn't highlight a problem with SquareD.
In conclusion -
Is it a GFCI incompatibility issue ? I don't know and Pentair refuse to comment !
Have the electronics gone crazy in the Pump ? It might be as the tech guy couldn't explain that peculiar start up sequence where it started and stopped for no reason.
So, I'm junking this over prices and worthless VS pump and fitting a simple 2 speed pump at 1/3rd the cost and while I'm at it, I'll have installed an Alexa ready Wi-Fi timer at waist height instead of getting down on my knees to use the crappy key pad that's on the pump. At least I can use my phone to change times if needed.
I forgot to mention, its a very noisy pump this Pentair pump compared to the ancient one that died in 2019 after giving good service. If anyone knows of a fix or suggestion, I'd welcome it.
Thanks - Mike