Planning Indoor Fiberglass Pool
mareas
11
Chihuahua, Mexico
Hello all,
We're planning our indoor pool (14x34x6) and spa (7x9x3) build in an area with no certified PB's and in an unregulated area however I've been trying my best to abide to US/International standards. I'd like to share the process we've made and ask for your valuable feedback!
Climate wise, we live around 6800 ft in elevation in an arid part of North Mexico, it can snow during the winter but have great summers, you can view here for an overview if it helps. The pool will be installed in a steel and block building which we can condition and dehumidify. The mechanical room for the pool will be in another building with better insulation however the heat pump is required to be installed outside.
Automation System: IntelliCenter with Salt Generator + 8 relays + 2 Actuators
Circulation System
Pump: Pentair SuperFlo (max 120 GPM, 13000 gallons) with 3" intake pipe and 2.5" system pipe.
Filter: A 300/400 sq ft cartridge filter (tbd but ideally with 2.5" connections)
Heatpump (shown as black square): AquaCal SQ120R with pressure bypass and manual bypass
Gas Heater (shown as white square): Pentair MasterTemp with manual bypass. As the temp drops below 50f for a few months overnight we'd like to use gas as a backup in the worst weather.
SWG: IC40
Intakes:
• 2x Hayward skimmers with equalization lines to wall mounted drains each with 2" to the pump
• Floor drain from Spa with a 2.5" line to the pump.
Returns:
• 4x 1.5" return jets in main swimming pool in a 2" loop supplied with a 2.5" pipe from the pump
• 6x Venturi jets (Hayward SP14343PAKA) with a 1.5" loop supplied with a 2.5" pipe from the pump
Jet System
Pump: Pentair Intelliflo 3HP (max 160 GPM) with 3" intake and output pipe.
Intakes:
• 2x Floor drain from Spa with a 3" line to the pump.
Returns:
Air Blower System
Air Blower: Air Supply of the Future Silencer Air Blower, 1.5HP
  1. Measure maximum height of water above lowest section of air channel = 2’ 10” or 34”
  2. For each 10 feet of 2" supply pipe, add 1" (inch) of water pressure = 21’ 6” = 4.25”
  3. For each 90 degree turn, add 1/2" (inch) of water pressure = 11 = 5.5”
Total water pressure = 43.75” = 1.5HP blower
Returns:
• 12x Venturi jets (Hayward SP14343PAKA) with a 1" loop supplied with a 2" pipe from the air blower.
Equipment List
TypeModelQuantity
Fiberglass Pool14x34x6 feet1
Fiberglass Spa7x9x3 feet1
Control SystemIntelliCenter® with Salt Generator + 8 relays + 2 Actuators1
Heat PumpAquaCal SQ120R1
Heat Pump BypassSTK01351
Gas HeaterPentair MasterTemp1
Salt Water GeneratorPentair IC40 (included with IntelliCenter)1
Cartridge FilterCJ-2750 Cartridge Filter (potentially different to have a 2.5")1
Water PumpPentair SuperFlo1
Spa PumpPentair IntelliFlo3 Variable Speed and Flow Pump 011075
Air BlowerAir Supply of the Future Silencer Air Blower, 1.5HP1
LightingPentair Microbrite Color LED 4 Light Combo Kit With Transformer 12V 300W 100' Cord, 6021331
Pentair Microbrite Color LED with 100' Cord 6204251
Three Way ValvesJandy 47174
Two Way ValvesJandy 47162
Check ValvesJandy 73052
Air Blower Check ValveAir Supply Silencer Check Valve 1/4 lb (included free)1
SkimmerHayward SP1084 2
Skimmer Float ValveSP1082FV2
Skimmer Equalization ValveSP10782
Skimmer Eq. DrainWG1049AVPAK2 (includes 2)1
Spa DrainWG1049AVPAK2 (includes 2)2
Spa Jet AssemblySP14343PAKA12
Spa Jet Fitting ToolSP1434T1
Whirlpool JetSP14372
Pulsing JetSP1436PAKB10
Wall fittings1.5" Hayward SP1023S, (4 returns, 5 lights)9
VacuumW3PVS20JST1
Skimmer Enclosure12" Hide Tiles 2
Waterline Tiles 6" x 12" x 100' Tile
Waterline Tile AdhesiveSilicon Rubber Adhesive
Waterline Tile GroutSilicon Rubber Grout
Solar Cover1
Pool Rail1
Questions
1. Would you recommend to use 1.5" for air instead of the 1"?
2. Does the two loops for the different pump returns make sense? I'm particularly concerned about the jet system going from 3" to a 1.5" flow through the manifolds.
3. Will it require a check valve on the spa return for the 6" height difference?
I would be working on the building before I even started the pool. You will need a good venting system as well as a way to remove the humidity from the building.
You also need to plan for how you are going to add/remove water from the pool with it being inside a building.
Thanks! The buildings designed and not as a worry. It’s got AC, dehumidifier and EHR with HVAC pro on calculations. Blower door tests etc. I’ll probably install a three way valve between the pump and filter for removing water. A water point close to the pool for cleaning and filling.
Reactions: kimkats
Get an Intelliflo3 pump and not a Superflo pump for the pool.
Superflow pump has 2” in and out, not 3”.
Get 011077 Intelliflo3 pumps with the control panel. It will make it easier to manually control the pumps when at the equipment pad.
Thanks, that helps a lot! I wasn't sure if the superflo would be ok for the circ pump on a larger tube size but I guess it can impact self priming?
I'd overlooked in the Air Supply manual it recommends 1.5" for the jet so I can make that change.
I've done some calculations here and the PSI seems well below the acceptable ratings. My only concern is head loss with 3" splitting into two 1.5". I could potentially split them into two loops with a 3" to two 2.5" connections that both connect to two 1.5" for each loop. Will it really sustain more flow or am I being pedantic though?
  • The dynamic pressure in the 3" pipe with 160GPM is approximately 11.41 PSI.
  • The dynamic pressure in each 1.5" pipe is approximately 45.69 PSI.
Still trying to understand this.
The Superflo VST pump would have worked okay but the Intelliflo3 will give you more flexibility with flow rates and work better.
On the spa jets you need to reduce the 3" feed pipe down to eventually nozzle size.
What air/water manifold will be used at each jet and what size pipe does the manifold take?
You should always have a CV in the spa return of a raised spa to prevent draining back to the pool when the pump is off.
They Jet manifold is Hayward SP1434PAKA with 1.5" water and 1.5" air which is looped with six jets on the jet pump. The return for the circulation pump also has six jets which I could put some onto this loop or create a second loop that so the 3" isn't going directly to 1.5"
If I have low floor jets would the same apply for the pipes which feed the jets?
That is fine.
You jumped from talking about the spa to the pool?
What do you need six returns in the pool?
I think we need to see some plumbing diagrams to see what you are describing.
Yes think I confused you there. For the circ system the pool has four returns and the spa has six jets. I've put it on a diagram to show more clearly.
Your diagram looks fine to me. Let's have @mas985 have a look.
I would use a 2.5" air line to the spa and then you can step down to the 1.5" lines when you split it for the two half loops around the spa. I am not a big fan of those fittings because they force you to use smaller pipe for the loop. My spa has 6 jets and there is 2.5" around the loop for water and 2" for the air.
Is the spa and fiberglass or a metal spa?
Have you chosen an insert for the manifold?
For 6 jets, 2.5" is minimum for the lines to/from the pump but I would go with 3" for both return and suction water lines and 2.5" for the air line from the pump. Also, you want to make sure a Hartford loop is installed close to the spa.
Will the venturi air line have a slope upwards or downwards from the spa to the equipment?
Absolutely. That is how my pool/spa is plumbed. Using the same pump for the circulation and the spa jets is not a great option because it forces high flow rate water through the filter and heater which makes the jets not as strong.
Yes
From the pics, it looks like there are only 4 lower venturi jets on the main pump which would make sense if you are running these off the main pump which has to go through the filter and heater so there is less flow rate.
Also, from the pics, it looks like there is only 1 MD for the suction line of the main pump. This is not to code. There should be a split MD for that pump as well.
If they are same venturi jets, then the plumbing is identical. However, if there are only 4 lower jets, then 2.5" to/from the spa for those is fine.
They are both fiberglass and should be "normal" as they are locally produced for export to USA.
Not disagreeing with your experience here but they specifically state 2" going into 1.5" for the jets on the 1.5HP Air Supply Silencer. Would you recommend an alternative model that recommends 2.5"?
I'm thinking of the whirlpool (SP1437) and pulsing jet (SP1436PAKB). The best brochure I've found with information is available here. It looks like the minimum is 10 GPM but I've not been able to find nozzle sizes and higher limits.
Thanks, I was having trouble fitting four in the floor of the spa with a 3' distance between each but I'll move the light somewhere else. I have seen the new hayward sump drains but do you know if there are any unblockable drain choices for fiberglass pools?
There is actually six (12 in total) but perhaps it would be better to separate them further for the different nozzles and to increase flow in those jet assemblies:
Jet pump: outputs to 8x pulsing jets at average of 160GPM or (20GPM per jet). I can split these 8 into two loops of 4 on the 1.5" tubing which would slightly improve
Circulation pump: outputs 4x whirpool jets acting as floor bubblers to max of 30GPM. I'd need to calculate the power loss through the equipment for the Intelliflo 3HP but the 2.5" piping would support up to 120GPM for this.
Yes, they are one type of "normal" spa jets just not the manifolds that I would choose. But given the spa is fiberglass, you are limited in what you can use. One way to get around the limitation is to split the return pipe in half and then half again so each branch is feeding only two jets. That way you are not trying to feed to many jets off of a single 1.5" line. That can cause jet flow imbalance leading to unequal jet performance.
They are specifying a minimum diameter for the air line. The connection does not need to be the same size as the air line since a bushing can be used to connect the two different sizes.
However, I would recommend a spa jet system without a blower. They are loud and use lots of energy and it is not hard to design a system without one. I don't have a blower on my spa and get plenty of bubbles without one. The key is to use large water lines and large air lines as well as a Hartford loop. Most PBs recommend blowers because they really don't know how to design a spa without one. Most don't have a background in hydraulics. ;)
How close is the equipment to the spa? Again, is there a slope change?
The higher the flow rate, the more the pipe size and air line size will make a difference.
.Thanks, I was having trouble fitting four in the floor of the spa with a 3' distance between each but I'll move the light somewhere else. I have seen the new hayward sump drains but do you know if there are any unblockable drain choices for fiberglass pools?
Would this fit:
Another option is to use wall mounted MDs.
So 4 jets on the main pump and 8 jets on the jet pump?
I don't think you will get 160 GPM on the jet pump with that configuration (see below).
I don't think you will get 120 GPM when going through a filter and heater. There is head loss in not only pipe, fittings & valves but also in the filter and heater and not to mention the jets which are very high in head loss.
I put together a head loss model to show you approximately how much flow rate you could expect out each loop.
The loop with 4 spa jets going through the filter and heater, the pump would likely get about 68.6 GPM or 17.2 GPM/jet.
For the spa jet pump with 8 jets, you will get about 130.9 GPM or about 16.4 GPM/jet.
If you upgrade spa jet pump to an Intelliflo XF, you can expect about 141.3 GPM or 17.7 GPM/jet.
I'm with you, I meant it to be read as a standard fiberglass pool and not below a common standard outside the US. Understand the point though and I'm not fixed on the manifold they are just often recommended with the fiberglass pools and hard to find alternatives. CMP might have a system where I can use a venturi tee (CMP 23306-100-000) into a 1.5" FIP x 1.5" Socket return fitting (25522-100-000) with a 1.5" FIP therapy jet (1.5" Therapy Jet Internals - CMP). It might increase the air flow? Would you recommend them as a reliable brand though? I've heard they were recently bought out and some lines are not going to be produced anymore so I was trying to align closer with the larger brands.
There is a guide here but not much useful figures: https://www.c-m-p.com/wp-content/uploads/2014/03/10000-300-247-Spamaster-1-5-Deluxe-Jet-SCREEN.pdf
20 feet and no significant change. That's for the mechanical room but I could easily build an equipment pad within a few feet if necessary.
Would this fit?
Unfortunately not. I really like them but they are all for gunnite pools. I'll try use a mix of wall and floor but four 8" drains in a small spa seems tight.
That's correct but not final if you recommend otherwise. I've also considered two bubblers in the spa instead of the four pumps but would that require a blower?
Thanks for those! I was hoping someone would help me with the spreadsheet later but this is really helpful.
That might work.
The exterior fittings only change how the jet moves. I like the spinners:
It might help with both air and water flow.
20 feet is fine.
That may be the best approach.
Yes, bubblers do require a blower because they do not have a venturi.
I modified it for the 20' lengths although it does not change much for just pipe length.
I've called around today which helped conclude a few points:
No venturi tees designed for fiberglass installs
At least for the popular brands which only use jet manifolds/bodies. The hayward might be a better alternative if this is the case as they have the 1.5" line rather than a 1" line for air. Internally in the bodies though I believe they both narrow to around 1/2" to 3/4" entry though but hard to get exact measurements from their support on this.
The 1.5" CMP jets aren't adjustable but the 2.5" spa jets would be.
The jet's linked above are also not able to be adjusted (water/air mix) and they recommend their 2.5" range (2.5" Spa Master™ Jets - CMP) for that purpose. If the flow is imperfect across the jets they can at least be adjusted.
There is a strip drain for fiberglass pools
Waterway provide the following unblockable strip drain with https://waterwayplastics.com/wp-content/uploads/807-0240.0410_reduced.pdf which is a huge improvement on four circle sump drains!
Based on your feedback I've made adjustments to align on your proposed method (I've not completed air lines yet). In the design:
  • 3" jet pump return line is reduce to two 2.5" lines
  • Each 2.5" line is reduced into two 2" lines
  • Each 2" line is split into two 1.5" line to feed a single jet body/manifold.
The circulation system:
  • 2.5" circ pump return line is reduce into two 2" lines
  • Each 2" line is split into two 1.5" lines to feed a single jet body/manifold.
It obviously looks far less elegant but having each jet on its own 1.5" line does make sense if that looks right to you?
I was also wondering if there is any good information on designing the venturi system without a blower? Is it virtually the same as with a blower but with a hartfood loop near the spa or is it worth separating the jets into sets to have an air adjustment valve?
Reactions: mas985
What matters more is how these are fed. Using the binary tree I outlined above will help prevent excess losses.
These layouts should work fine. The last TEE before the jet body can be done between two jet bodies to simplify the layout and eliminate the need for additional fittings.
When a blower is used for a venturi jet, in most cases it is used to help clear the air line of water. Most PBs do not use a Hartford loop at the spa so what happens is when the jet pump is shut off the entire length of the air pipe fills with water and then when the pump turns on, it is too much water to clear. So instead of designing the air line so it does not fill with water, the PB uses a blower instead to help clear the lines. But the problem that I have seen on this forum is that the blower ends up adding too much air to the air lines and the bubbles tend to blow water up on the deck.
For the design of a spa without a blower and with long air lines, it is the Hartford loop that is key. However, if the outlet of the airline is within about 15' of the spa or the air line slopes upward away from the spa, then in most cases, even a Hartford loop is not necessary. The point is to prevent a long and deep section of the air line from filling with water.
However, if you want air adjustments for the air line, then I would put in a spa side valve for each spa jet so everyone can have there own air line adjustment. In this case, no Hartford loop is necessary and the air line loop around the spa goes away. The air lines for each jet simply go upwards to the deck where a twist valve allows adjustment for the jet air. This is very similar to how standalone spas handle air adjustment. There are many different styles for this but here are a few examples:
The type you use will depend on exactly where it is located.