Hi All,Heater keeps flashing Cool Down, and the valve will not open the bypass. I can cycle the power to the heater, and everything resets, and the same thing happens again. I matched the cool down setting in IC to 1 min, to see if that worked, it did not.
So at the moment, I am at a standstill on the on-board heater bypass valve until I can get in touch with Pentair support. Wondering if anyone out there who has a later model heater with this functionality, and has it running, has seen this?
It has been some time that we've had this cooldown issue with the Connected MasterTemp heater and the use of the auto by-pass IntelliValve connected to the heater's control board (not to the IntelliCenter). I've been somewhat persistent with Pentair to get it addressed (I did not have a spare slot for another IntelliValve on the IntelliCenter). Pentair had sent me a version 2.00 Heater Control Board, but that did not solve the problem! Finally I received from Pentair a custom board to test. I installed the board and it worked. The heater no longer got stuck on Cooldown!! I checked numerous scenarios and they all worked. I did have an issue when I switched off the spa, while calling for heat (more on that below, as it does not seem to be cooldown related). All the following scenarios work:
1) Set Spa On, select MasterTemp heater, Set desired temperature above current actual. Action: Bypass deactivates, and Heat is called. (this is the only scenario that previously worked).
2) Once the Set/desired temperature is reached. Action: call for heat is stopped (heater goes idle), Cooldown is triggered (1 minute), bypass is automatically triggered
3) When actual heat falls below set/desired temperature or manually increased. Action: Bypass is automatically deactivated; heater calls for heat again.
4) If I switch off the MasterTemp heater (not the Spa) while calling for heat. Action: Pump continues to work, Cooldown is triggered, bypass is automatically triggered after cooldown.
From my perspective this is working well. Since this was a one-off Heater Control Board (Version 2.00 plus enhancements), I would imagine that one would need to wait for the next official version of the board. By the way, I'm using IntelliCenter Firmware version 2.017.
Now to the issue and may be there is some guidance from TFP members as it might be an IntelliCenter setup issue.
If I switch off the Spa mode while heater is calling for heat (Heating red light on membrane pad is on). The pump switches off immediately. On the heater - even though no water is flowing - it still goes into cooldown mode and after about 1 minute the bypass reactivates. IntelliCenter did not keep the pump on while the heater completed its actions. FYI, I do have cooldown set to 1 minute on the IntelliCenter, even though - I understand - the MasterTemp does not use that setting and has a fixed 1 minute cooldown period. Any guidance on this issue? If my setup is all good, I will follow-up with Pentair.
Very happy that this bug has finally been addressed! It had been quite irritating having to power cycle the heater after each use of the Spa in order to reset the bypass!
Copying a few on this post, as they had previously expressed an interest in this topic.
@Turbo1Ton @rstrouse @tomas21 @kracklow @pskkd930 @MyAZPool @kraigkoobs @thezookman @KevMo @ajw22 @Ahultin @Turbo1Ton
Tony